R

Robo

Curiosity strikes again. I keep going to site and seein tempory generators. Do all of these require earth spikes?? And is a specialist earth electrode tester needed to test these or can you test Ze at main switch to see if its within its tolerance.. Whats the maximum reading etc.. Thanks
 
should really be an earth spike, but nobody seems to do that.....I have seen somebody before dragging a small wheeled diesel generator around behind them by the extension lead to run a lawnmower, using a smashed up old start-stop pushbutton switch to turn it on and off with the wires hanging out they thought it was ok because "its not mains ok" was waiting for them to get a belt off of it....
site generator should have an earth spike connected to its metal frame, which the earth terminals are connected to, have only seen one on a site before with a 150kva machine, it was a nice shiny copper corkscrew shape with a handle to twist it into the ground and a cable clamp on it....only ever seen one used...
 
Could you explain the floating earth part to me please?? So it is recommended the genny has an earth stake or connected to building structual steel work os this need to be tested etc?
 
This is taken from the file I attached above and explains it better than i can. But a floating earth is basically an earth connection at a socket on the generator that is not referenced to the neutral of the generator winding.


LOW -VOLTAGE, SINGLE-PHASE PORTABLE AND TRANSPORTABLE GENERATORS
7 These are generally machines ranging in size from 0.3 to 10 kVA. Winding connections are brought out to a socket, in which the third or protective conductor socket tube is usually connected internally to the generator enclosure but may in some cases be referenced internally to one pole of the generator winding. A voltage-selector switch may be fitted to enable 240 V or 120 V outputs to be obtained from BS 4343 sockets of the appropriate type.
8 Where there is no path for earth fault currents to return to the 'separated' winding of a generator (cf the secondary winding of an isolating transformer), it is acceptable for these small generators and their loads to be run without deliberately connecting either external metallic parts or one pole of the single-phase electrical system to earth, subject to the following conditions.
(1) Only cables which are suitable for their environmental exposure should be used to connect the generator to its load. The use of PVC-insulated and sheathed cables with flexible, braided wire armour and a PVC over-sheath is recommended.
(2) The generator enclosure should be bonded to all other metallic enclosures which form part of the system (eg to the metallic braid of flexible cables and the load enclosures if metallic), by correct termination of the protective conductors and braids.
(3) If flexible cables without a continuous metallic braid are used, suitable 3-core cables should be selected with an extruded over-sheath capable of high resistance to abrasion or damage.
(4) All cables require frequent inspection. Users should be alert to risks which arise from damaged cables which should be replaced and not repaired, and from
 
Last edited:

Reply to Generator earth spike in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I used 9mm earth rods with a right angle bend on the top and earth wander leads suitably sleeved to denote the different positions, worked out a...
Replies
1
Views
639
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
963

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top