Hi Trainees,

I'm a bit of a novice with electrics and I'm scared to post on the main forums so I thought I'd get some help here. :D

I have an existing installation which is a pump house with several pumps in it. It has a DNO supply via a meter box which is about 155 meters away via a 25 mm² 4-core SWA cable.

I need to install a small 3-phase generator for power back-up which has a max output of 70Amps per phase. It's mountainous terrain and the closest we can locate the genset to the pump house without using a helicopter is 175 meters downhill from the meter box.

We're going to locate the Automatic Transfer Switch at the existing meter box location so I need to run a 4-core SWA cable which will be buried direct in the ground between the genset and the meter box.

Please help me work out what size SWA cable I need and also show your method of how you reached your answer.

Thanks in advance for your efforts.
 
[ElectriciansForums.net] Generator Installation, Help Please.
 
No takers?

I could do with some assistance on this please so I can get my cable ordered.

If you need any more info about the installation just ask.
 
Hi Marvo, why 4 core for the existing cable to the pump house, Have you used two cores for line and two for neutral?

Will have a go at this later today as I’m really rusty on it now.

Got to swap engines in my transit first as it’s melted another piston :tearsofjoy:
 
The whole installation is three phase isn't it, even though your diagram shows a single phase head?
Your diagram also seems to show, as one would expect in a remote area, that the supply is locally earthed forming a TT earthing arrangement at the service head.

Hmm, seems difficult, I think you will have to ask on a forum to get an answer, perhaps some trainee could help!o_O:rolleyes:
 
Hi Marvo. I'll try give me a nudge in the right direction.

ib ≤ in ≤ iz
I assume ib=70amp
Cut out fuse? I'll assume it to be 80amp
Reference method D
Thermoplastic or thermosetting
Ground temperature? 20 degrees c? Am I barking up the wrong tree? I am not sure.

Let's say in ≤ iz thus iz=80a

Thermoplastic Table 4D4A volt drop table 4D4B
Thermosetting table 4E4A volt drop table 4E4B
I reckon it could be either 25mm or 35mm depending on volt drop. I don't know whether to apply +10%/ -6%.
 
Hi Marvo. I'll try give me a nudge in the right direction.

ib ≤ in ≤ iz
I assume ib=70amp
Cut out fuse? I'll assume it to be 80amp
Reference method D
Thermoplastic or thermosetting
Ground temperature? 20 degrees c? Am I barking up the wrong tree? I am not sure.

Let's say in ≤ iz thus iz=80a

Thermoplastic Table 4D4A volt drop table 4D4B
Thermosetting table 4E4A volt drop table 4E4B
I reckon it could be either 25mm or 35mm depending on volt drop. I don't know whether to apply +10%/ -6%.

Vd would be the same for 25mm and 35mm @ 1.77V (thermoplastic)

If using thermosetting cable I’d say 25mm would be suitable. Vd would be very similar @ 1.71V
 

Reply to Generator Installation, Help Please. in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top