We have a switch cubicle which is being taken out and
replaced with a new one as part of extensive building
works.
The exist cubicle at the moment only supplies another
large building with a 240mm 4 core swa and a supply
to construction site cabins and a local tpn board.
A company is coming in to disconnect the public supply
to the existing cubicle so it can be taken out,whilst
the new cubicle is being fitted the supplies that were
being used are to be temp fed from a 150kva 400v generator
situated out doors.
As a matter of interest what would be the supply type ,can it be tns or tt and how do you earth it with regard to
the already fixed installations it will supply and
do you need rcd protection where there was none before
when connected to the public supply and what is max ze
or earth electrode resistance.
sorry to be so long winded but would like to no as a matter
of interest.
 
Hi there.

There is no problem with using the TN-S supplied from the generator to supply the existing installation during switchover.

As always the gen frame should be rodded to earth, and as a matter of precaution I always install a rod at the distribution board you are supplying as a just incase.

You just need to make sure that the earth is "floating" inside the geney as if it is strapped to neutral (larger geneys usually are) this would give you a TN-C-S supply and obviously different rules apply with regard to earthing and bonding and the use orf RCD's, best to leave as TN-S.

Obviously the geney will have an RCD upfront, usually along the lines of 100mA (sometimes adjustable) this would then protect all of the existing installation.

Ze/Zs will be the same for a mains powered installation as you still need to be able to achieve the same disconnection times i.e 100mA RCD on TT = 500ohms. As it will be a TN-S though you should be looking at max Ze of 0.80ohms.

Hope this helps.
 

Reply to generator regs in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

I don't think I'd use it mate even the one line heading then one long paragraph screams ai. And untrustworthy. I don't think much has been edited...
    • Optimistic
Replies
3
Views
795
  • Question
Lucien, the open framed generator that goes with your engine is just generator ---- but I feel we are going to end up with a separate discussion...
    • Like
Replies
3
Views
1K
  • Locked
  • Solved
Therein lies the problem. I see no merit in further circular debate, so will bow out of this discussion.
    • Like
2 3
Replies
55
Views
7K
nicebutdim
N
  • Question
The DNO have been out this morning and said that the connection is PME, and both the braid and wire together are part of the system. They've...
Replies
24
Views
7K
  • Question
As a former telecoms engineer id also prefer people didn't use grey!!! ?
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks