House built in CA, in 2004. 15 amp GFI in the garage that runs exterior outlets keeps tripping. Things I have tried to troubleshoot:
1) I replaced the GFI, and still trips after approx 10-15 seconds
2) Unplugged everything in all the outlets (7), and it still trips
3) Removed the GFI and direct wired the power and all the outlets downstream work without tripping the breaker at the panel
4) Reconnected the GFI, WITHOUT hooking up the load side, and it works without tripping (tells me the GFI is not the problem and the issue is downstream of GFI??)
5) checked all of the outlets downstream of GFI for moisture, and the boxes are dry.
6) Hooked the load side of the breaker back up and it trips the GFI again after 10-15 seconds.

I am at a loss for what to do next or what the problem could be. Any help is greatly appreciated.

Thanks!
 
House built in CA, in 2004. 15 amp GFI in the garage that runs exterior outlets keeps tripping. Things I have tried to troubleshoot:
1) I replaced the GFI, and still trips after approx 10-15 seconds
2) Unplugged everything in all the outlets (7), and it still trips
3) Removed the GFI and direct wired the power and all the outlets downstream work without tripping the breaker at the panel
4) Reconnected the GFI, WITHOUT hooking up the load side, and it works without tripping (tells me the GFI is not the problem and the issue is downstream of GFI??)
5) checked all of the outlets downstream of GFI for moisture, and the boxes are dry.
6) Hooked the load side of the breaker back up and it trips the GFI again after 10-15 seconds.

I am at a loss for what to do next or what the problem could be. Any help is greatly appreciated.

Thanks!
If you did everything that you said then could they possibly be a staple drove through one of the cable’s. I’m understanding that it’s one 15 amp circuit and just 1 cable in and 1 cable out and with no other neutrals involved, then I’m stumped
 

Reply to GFI Tripping in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
444
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
338

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top