Hi to all..have heard some people talk about a basic '1st' test regarding a possible cu change , called a global ir test. I understand that this that this a test performed on all circuits which may assist in determining if a fault is present before delving into the indivdual circuits.
Being new , i have not done one , or been present when someone else has done one.
Can someone piont me in the right direction re method and principles behind it ?
Not that i am going out to perform tomorrow , but i might get a couple of expirienced electrians to talk me through it.
Always helps to have a bit of understanding beforehand.....

Thanks to all as usual
 
Suppose your CU has one RCD. Remove all loads and sensetive equipment then with test probes on the load side of RCD and all MCBs in the on position send your test voltage in. Acceptable IR result is in OSG and GN3.
 
and if there's no RCD, swsitch main switch off. you perform an IR test between each L and E and then between the N and E bars. obviously you then have all the neutrals and Earths in parallel so expect a reading less than for individual circuits.
 
If following the above tests make sure ALL appliances are unplugged or isolator switches off.

Alternatively for an indication of condition, link the line and neutral then test to earth.
 
and after you do the above mentioned tests known as a "block" test if you have low IR readings test each circuit individually to narrow down your search for the cause of the low resistance

(youd do this first of all by turning the mcbs off and testing the load side of each circuit to earth or by removing neutrals individually and testing to earth etc)

and the reason youd do this as youve mentioned to avoid any issues installing new equipment for example if your installing rcd protection the condition of an old circuit which has only previously had fuses/mcbs the leakage will affect the rcd and trip it if there is a problem with the circuit etc
 
Last edited by a moderator:
Hi wa209

If you do perform a globle IR test as mentioned above be aware of any surge protection devices plugged in around the premises when testing at 500 volts as they will see the high voltage and dump it to earth giving you a false reading on your test.

IMO I would always soft test at 250 v in the first instance .
 

Reply to global ir test ??? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

There is a lock on it, press the test button down and press the lock button, the symbol will appear on the screen in the middle right hand side...
Replies
5
Views
471
  • Question
There can be a few reasons for low L+N -> E readings: Connected equipment is leaking. By design, or just old/damp SPD are connected (but there...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top