Anyone know where I can get a free copy of IET GN8?
 
I didnt think so, thought there might Be a download somewhere, £30 for a copy.
 
What I'm looking to understand is sub main earthing conductors. Is what I am saying right?

So a sub main to an installation not requiring bonding the earthing conductor can be determined using the Adiabatic equation or table 54G

However a sub main which requires a protective equipotential bonding conductor, to say a steel framed shed, this is determined by the size of the suppliers neutral conductor using tab 54.8 if PME or half the size of the main earthing conductor min 6mm not exceeding 25mm.

In this situation would your earthing conductor be the armour or a core of the supply cable and run the separate bonding conductor straight to the structural steel, water or gas? Or would you take it to the Sub main distribution board and them from there to the structural steel? Does this make the the earth terminal in the DB a EMT?

So if you had a PME supply with 95mm incoming neutral and the sub main requiring bonding to structural steel was a 5 core 16mm you would run a separate 25mm earth wire to the structural steel.

Is it as simple as that?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Scotland
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
GN8
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
Rocboni,
Last reply from
Rocboni,
Replies
3
Views
98

Advert

Back
Top