AdamKerr88
I'm on a job at the moment in a old detached house that has been converted into a office share building ( 6 small offices that would suit 1-2 people per office) this is spread over 3 floors and includes two small tea stations.
The customer has their own safety company involved who have told the client that a mains powered interlinked system or grade d system would be sufficient protection for the building, they have requested that the detectors are placed on landings and inside offices. The are no detectors spec'd for the two tea stations and nothing in the areas that form part of the fire escape route and no break glasses at the exits.
I re spec'd the system with a conventional panel and the detectors installed to LD3 ( detectors in landings, escape routes and break glasses at each fire exit etc but no detectors in the offices). They have come back to me and asked for the grade d system to be installed as per their guys specification.
Personally I have only seen grade d systems (or part 6) installed in dwellings, in my experience they are not installed in commercial properties as they don't meet the requirements of bs5839 for a building used for this purpose, no call points etc.
Has anybody ever been asked to install or has installed one in a small commercial property ?
The customer has their own safety company involved who have told the client that a mains powered interlinked system or grade d system would be sufficient protection for the building, they have requested that the detectors are placed on landings and inside offices. The are no detectors spec'd for the two tea stations and nothing in the areas that form part of the fire escape route and no break glasses at the exits.
I re spec'd the system with a conventional panel and the detectors installed to LD3 ( detectors in landings, escape routes and break glasses at each fire exit etc but no detectors in the offices). They have come back to me and asked for the grade d system to be installed as per their guys specification.
Personally I have only seen grade d systems (or part 6) installed in dwellings, in my experience they are not installed in commercial properties as they don't meet the requirements of bs5839 for a building used for this purpose, no call points etc.
Has anybody ever been asked to install or has installed one in a small commercial property ?