Got called to a fault at commercial premises yesterday and thought i would share what i found.
The initial call was to an isolator which was worn and kept going off so did the usual isolation and was a bit confused as breaker was single phase and isolator was tp&n,
took cover off and found out originally it was a 16a three phase supply and the machine was replaced with a 32a single phase version (think you know whats coming).
It was 2.5 singles run in pvc conduit 3xred with cpc. two red's doubled up and red and cpc doubled for neutral, the earth was hopped off another circuit nearby. The funny bit about it was the sparks altering it had sleeved the reds with brown tape and the black & cpc with blue.
The board was only three metres away so could have changed it easy, why do these people bother. :lol:

I should have said this was done by a large electrical company but i mention no names, but if your reading this, i got your number.
Gave me a laugh at the time but then had to think of a way to explain to the client.
 

Reply to Great alteration in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
none at all.... and the rcd trips within specification... test button operational.... nothing to suggest there's a problem until you take the...
    • Like
Replies
2
Views
512
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K
Hello Ric2013, MJPD29 and westward 10. I have a multimeter that I tested the voltage with and before I open the socket up I use a plug in tester...
Replies
4
Views
1K
  • Question
Yes I noticed that too, although the Fluke 1664 that I use claims the same precision (it has a milliohms mode in the high current loop impedance...
Replies
18
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks