robsparky1975

JUST A QUICK QUESTION,WELL HAVE YOU GUYS SEEN GREEN RESIDUE IN OLD CABLES BEFORE,MUST BE 60s WIRING,SEEN A BIT BEFORE ON CABLES BUT TODAY,IT CAUGHT MY EYE,WEEPING DOWN KITCHEN WALL SOCKETS,CEILING ROSE TERMINALS VERY GREEN,IS THIS HOW THEY USED TO MANUFACTURE THESE CABLES,WITH GUNK IN THERE?NEVER SEEN IT THIS BAD,ANY THOUGHTS,DONE INSULATION TEST ON IMMERSION CIRCUIT ALL FINE,JUST HAD TO REPLACE A SWITCH,BONDING ALL IN PLACE,JUST WONDERING WHAT PEOPLE THOUGHT OF THIS.
 
Found this about it.

Green gunge is most prevalent in cables made between 1965 and 1971. The
gunge is degraded di-isoctyl phthalate and is the result of the reaction
between the plasticisor in the insulation and the copper. Between 1965 and
1971 the temprature performance of PVC was uprated by the inclusion of an
anti-oxidant in to the PVC. An unappreciated side effect was that the
anti-oxident encouraged the production of exudate.
Evidence suggests that that high ambient temperatures accelarate the
process. The exudate is of low flammability and low toxicity. Although
unsightly it does not reduce the electrical integity of the conductor or the
insulation.

See also the draft BCA statement (April 2001) below: -

1) PVC
PVC comes in two main grades, plasticised and unplasticised PVC.
Unplasticised PVC (UPVC) is used for example in double glazing window frames
where a rigid material is required.
The PVC used for manufacture of cables is a plasticised PVC that conforms to
the relevant British Standard for the cable type in question.

2) Ageing effects
As a cable ages; (at temperatures above normal ambient), the elongation to
break decreases (also the Insulation Resistance increases). The life
expectancy of a cable is arbitrarily considered to be when the elongation to
break of the PVC is 50%.
A lower elongation to break value could be considered suitable especially
for a fixed wiring cable. Therefore, providing the cable is not subject to
movement or when moved due to inspection of socket outlet or the like, the
PVC does not crack, a much lower value of elongation to break is considered
by some as suitable.

3) Greening
Greening is the appearance of a wet green substance that is a product of an
adverse reaction between certain types of plasticiser and the copper
conductors. This greening, which is a rare occurrence, can happen either
after a long period of time for some cables, or if the cable has been
severely overheated.
The plasticiser itself is a clear oily liquid that is non conductive. The
green substance is a combination of copper oxide and plasticiser which may
become conductive under certain adverse conditions.

4) Action if Greening is found
Therefore whenever this green substance is found at socket outlets etc.
initially it should be removed and the terminations cleaned (gloves should
be used) otherwise it is possible that tracking/overheating may occur. It is
strongly recommended that rewiring should be carried out as soon as
possible.

If further information is required, the original cable manufacturer should
be contacted
 
Thanks mate your a diamond,ive just left a post on the other green goo thread,how what can this stuff do to you? Apart from make your eyelid burn when you rub it like i did,i might end up like that bloke out of robocop,shhhhllllepppppp me
 
i'VE COME ACROSS GREEN SLIME SEVERAL TIMES, MOST RECENTLY IN THE HOUSE MY SISTER HAS JUST BOUGht. Ah, thats got rid of caps lock. According to the test sheet for the bathroom installed 3 years ago IR tests were 23Mohms, when I tested it the IRs were 0.3Mohms. If green sliming causes a degradation of plasticiser, surely the integrity of the insulation is compromised, thjerefore making the installation unsafe. I'm probably going against official non scaremongering advice but recommend rewire every time. Visual evidence of insulation degradation, time limits are the only valid argument. (That and being too tight to pay for safety)
 
i agree with re-wire,as i said to homeowner but they were 90 and 81 respectivey so the 90 year old just laughed and said i might not be around when it all starts to pop fuses time after time.
 

Reply to green residue in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
614
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

Being pedantic, the Crabtree 50A cooker switch is a 4500/1, which has 'cooker' printed on it. For a shower, you require the 4500, which is the...
Replies
3
Views
405
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
422

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top