Ok, forget about diversity and unlikely loading conditions for the moment.
A grid switch assembly with 3 DP switches each supplying 3kW loads.
Now if the Grid switches are at the centre of the ring then we would expect 37.5A available when all the loads are active and for a DC supply 18.5A divided between the outer two switches supplying 12.5A to the middle switch but as its ac current the current flow across all of the input terminals would 37.5A, 25A, 12.5A every 10ms then the same in the opposite direction for a further 10ms continuing until the loads are switched off.
If the grid switch assemby is ofset in the ring then the current flow through the switches would be proportionally more on one side of the ring.
The input terminals are therefore loaded by the loads throughout the ring.
very important to make sure the terminals are tight.
A grid switch assembly with 3 DP switches each supplying 3kW loads.
Now if the Grid switches are at the centre of the ring then we would expect 37.5A available when all the loads are active and for a DC supply 18.5A divided between the outer two switches supplying 12.5A to the middle switch but as its ac current the current flow across all of the input terminals would 37.5A, 25A, 12.5A every 10ms then the same in the opposite direction for a further 10ms continuing until the loads are switched off.
If the grid switch assemby is ofset in the ring then the current flow through the switches would be proportionally more on one side of the ring.
The input terminals are therefore loaded by the loads throughout the ring.
very important to make sure the terminals are tight.