The bit about cable entry, makes it clear IMO; there are no additional measures required for cable entry under A3, than there was for the previous amendment, i.e. intumescent seals etc. The panel members consisted of IET, Elecsa, Napit, Hager manufacturer and another person (who I didn't who he was from because of the poor sound quality at the start). They were all in agreement, however.
This reg change is not helped by differing interpretations of 421.1.201, with G4 suggesting the interpretation is fire containment and bodies like Elecsa/NICEIC etc interpreting it as removing the fuel from any fire. IMO, I can't see any benefit, by taking extra measure to 'seal' a A3 CU, when there's a dirt great loose flap on the front covering the MCB's etc.
The talk about grommets, is depending how they are installed would not comply with reg 416.2, horizontal/top (if accessible) IPXXD/IP4X & sides/bottom IPXXB/IP2X, i.e. you made the hole in the grommet too big!
Trunking, rear entry and even good old plywood are still acceptable methods of entry.
The glands mention in this thread, like the Wiska Sprint, are a necessity in TT supplies, but I still wouldn't rule them out in TN supplies, if not using the methods above.