Its good to asking a tech question rather than talk about FITs!

I have been to look at a job on where the panels will be ground mounted using Renusol Consoles. The array will be 10 to 12 metres from the property. The owner has asked for the inverter to be located in the garage. The fun bit is safely connecting between two rows of consoles and bringing the strings underground to the garage. I have been looking for flexible armoured conduit and only found any in the U.S. Has anyone any ideas or experience of this or know of a suitable supplier?

In many ways the easiest thing is to mount the inverter beside the panels and run SWA. Would still need safe connection/cable protection between the two rows of consoles.

Any thoughts?

Thanks
 
If you read the regs regarding an underground cable it specifically says:
'Except where installed in a conduit or duct which provides equivalent protection against mechanical damage, a cable buried in the groundshall incorporate an earthed armour'

So maybe you can get away with using something other than armour cable if you provide enough mechanical protection, eg, ducting + paving slabs (maybe)
 
SWA DC runs into an IP65 joint box with solar cable tails coming out, just make sure the array mounts are all bonded etc etc, don't forget to check on PME regs for connecting external metalwork to MET
 

Reply to Ground Mount Transfer of DC cable to Property in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
613
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top