hi all, the job i am doing for my first assesment is garage supply in conduit(i have previoulsy posted about that) and replacing the c/u, on assessing the job today for the c/u all of the cables come down from the ceiling in a wooden box covered with a wooden front, i removed the front cover off to inspect and all the cables are just bunched together none of them clipped, there isn't much room in there when the front is on there is roughly about 12 cables, my main concern is there is a 6mm cable roughly about 15m there running a 8.5kw shower which works out 37A load for the cable which i will have to put on a 32A mcb according to the regs i have to apply a 0.45 factor for 12 cables together,could someone please advise on how to do this calculation, so i can work out if it takes my cable rating below 32A, or my other option is to extend the box work so i can clip each cable seperatley which would then be classed as method c as there in no insulation covering any of the cables, would it still be classed as method c with it having wooden front, sides and back cheers