Hi, I have a dual RCD board made by Hager installed a couple of months ago.
It is high integrity, which I understand to mean RCBO’s can be fitted as well. (I got an EICR and let’s just say it was awful. The electrician who did the EICR even wrote a report for me but that’s another story).
After the posts on here I want to go full RCBO, and it seems this board allows it.
So that I vaguely know what I’m talking about when getting an electrician in, am I correct in thinking he or she would disconnect the RCD cables and then remove from the busbar. Then where the RCD was, the busbar would be left without a mcb/ RCBO, and a blank fitted, to prevent any fingers going in etc.
Or where the rcd was, can another RCBO be added ? Or should it just be kept blank as above? Basically what should be done to make it a RCBO board?
Board
Lastly I’m having solar PV fitted, it seems that everyone is having just standard type A, B curve RCBO’s put in:
Obviously this is for their electrician to do, but a bit of pre-planning.
I looked in the manual, and they just refer to a ‘breaker’ I read a thread several years ago that referred to needing a type B breaker due to DC current, but I thought it is a bit odd as the power coming from the inverter into the house, should be AC and there should be no or little DC leakage.
I have a second DB, which was installed in 2012, It’s a plastic Hager, 6 circuit board, with 4 circuits. I want to replace this with a board with SPD, and RCBO’s, I will buy a bigger board, and the solar will go on here.
The inverter is 5kw, (410 x13 panels) so 5.3kw (never going to get that).
Lastly the battery, which can discharge at up to 5kw/h and likewise charge at 5kw/hr. Is right on the borderline in terms of breaker size. I found that Hager do 25 amp breakers which would be ideal, or do you think they will just whack 32 amp breakers in ? I assume if they use a big enough cable it’s fine.
Thanks for any advice.
It is high integrity, which I understand to mean RCBO’s can be fitted as well. (I got an EICR and let’s just say it was awful. The electrician who did the EICR even wrote a report for me but that’s another story).
After the posts on here I want to go full RCBO, and it seems this board allows it.
So that I vaguely know what I’m talking about when getting an electrician in, am I correct in thinking he or she would disconnect the RCD cables and then remove from the busbar. Then where the RCD was, the busbar would be left without a mcb/ RCBO, and a blank fitted, to prevent any fingers going in etc.
Or where the rcd was, can another RCBO be added ? Or should it just be kept blank as above? Basically what should be done to make it a RCBO board?
Board
I’m pretty confident that this board can become a RCBO board, simply by removing the RCD’s and MCB’s, and then using RCBO’s. Am I correct ?
HGVML914CUSPD
Lastly I’m having solar PV fitted, it seems that everyone is having just standard type A, B curve RCBO’s put in:
Obviously this is for their electrician to do, but a bit of pre-planning.
I looked in the manual, and they just refer to a ‘breaker’ I read a thread several years ago that referred to needing a type B breaker due to DC current, but I thought it is a bit odd as the power coming from the inverter into the house, should be AC and there should be no or little DC leakage.
I have a second DB, which was installed in 2012, It’s a plastic Hager, 6 circuit board, with 4 circuits. I want to replace this with a board with SPD, and RCBO’s, I will buy a bigger board, and the solar will go on here.
The inverter is 5kw, (410 x13 panels) so 5.3kw (never going to get that).
Lastly the battery, which can discharge at up to 5kw/h and likewise charge at 5kw/hr. Is right on the borderline in terms of breaker size. I found that Hager do 25 amp breakers which would be ideal, or do you think they will just whack 32 amp breakers in ? I assume if they use a big enough cable it’s fine.
Thanks for any advice.