Today we got our Hager meter kit for one of their 125A TPN boards. It has a little DIN rail fuse holder as the meter is powered right off the incoming isolator/RCD/etc without any MCB for protection (so the meter can't be switched off without everything going off, presumably so you don't cheat on any internal billing but that means).
So I opened it up to look at the fuses and was rather shocked to see a 0.5A glass LRC fuse! You know, the sort with a breaking capacity of 35A at 250V AC! This is off a 400V TPN board that could have a 10kA fault current at that point FFS!
Even replacing the fuse with a 20x5mm HRC fuse is only good to 1.5kA fault rating. What were the product designers thinking?!
So I opened it up to look at the fuses and was rather shocked to see a 0.5A glass LRC fuse! You know, the sort with a breaking capacity of 35A at 250V AC! This is off a 400V TPN board that could have a 10kA fault current at that point FFS!
Even replacing the fuse with a 20x5mm HRC fuse is only good to 1.5kA fault rating. What were the product designers thinking?!