Hi all!
so I a chippy I work with installed a little kitchen, all appliances supplied from howdens - this particular brand is Lamona.
existing 32A ring was extended to pick up a few items (mini extractor, built in microwave, the hob and a countertop twin socket. Circuit tested out fine - a good R1R2 and a clear >1000M on IR. also tested the RCD for a solid result and ramp tested it to a comfortable 28mA operating current. I have not used an earth leakage monitor as I don’t have one.
however, the RCBO is intermittently tripping... I’ve isolated it down to the hob. I’ve had the hob running at full load and it’s fine, but every now and then when it’s not on (but energised) it drops the breaker off. Can’t get in touch with Lamona (a part of howdens that offer next to no technical support) so I thought I’d offer it out to anyone who may have had similar problems before and may have found a solution before I airmail the hob out of the window.
Thanks!
so I a chippy I work with installed a little kitchen, all appliances supplied from howdens - this particular brand is Lamona.
existing 32A ring was extended to pick up a few items (mini extractor, built in microwave, the hob and a countertop twin socket. Circuit tested out fine - a good R1R2 and a clear >1000M on IR. also tested the RCD for a solid result and ramp tested it to a comfortable 28mA operating current. I have not used an earth leakage monitor as I don’t have one.
however, the RCBO is intermittently tripping... I’ve isolated it down to the hob. I’ve had the hob running at full load and it’s fine, but every now and then when it’s not on (but energised) it drops the breaker off. Can’t get in touch with Lamona (a part of howdens that offer next to no technical support) so I thought I’d offer it out to anyone who may have had similar problems before and may have found a solution before I airmail the hob out of the window.
Thanks!