Dont do a great deal of commercial so just want to check on next job:
its a new business so as usual money is tight
want 3x hand driers for toilets (restaurant) they paid quite a bit for them (on lease i think) and were told they needed a spur from ring for each drier.
they dont know the exact details of the dryer but from the info i got i think 16kw each and two would need to come from same socket so a 13a fcu feeding two and a bit much for ring after adding other dryer and everything else on the ring.
So suggest new circuit but they cant have any chasing (as usual) so new 2.5 radial on 20a feeding all three dryers (bit close to ib but they unlikely to be on at same time or for very long)
anyways surfacemount outlets and labelled as dryers and cable run in trunking to 20asquared (as there is a spare 20 at db)
do you think rcd/ bo would be necc.
Normally as its surface and labelled i would say no but with it being in public toilets id say yes but looking for cheapest option.
its a new business so as usual money is tight
want 3x hand driers for toilets (restaurant) they paid quite a bit for them (on lease i think) and were told they needed a spur from ring for each drier.
they dont know the exact details of the dryer but from the info i got i think 16kw each and two would need to come from same socket so a 13a fcu feeding two and a bit much for ring after adding other dryer and everything else on the ring.
So suggest new circuit but they cant have any chasing (as usual) so new 2.5 radial on 20a feeding all three dryers (bit close to ib but they unlikely to be on at same time or for very long)
anyways surfacemount outlets and labelled as dryers and cable run in trunking to 20asquared (as there is a spare 20 at db)
do you think rcd/ bo would be necc.
Normally as its surface and labelled i would say no but with it being in public toilets id say yes but looking for cheapest option.