Discuss Has this consumer unit been installed correctly? in the UK Electrical Forum area at ElectriciansForums.net
That back board needs replacing.
Cheers Charlie_
Revenge!
Done a board swap for my nephew last week.
Was disappointed when I seen he had bought proteus/m2 but I was pleasantly surprised with the product..
The case is not as good as Hager or Wylex but the terminations are good, I prefer the fork style busbar
View attachment 49451
View attachment 49452
The regulations now require that the main switch and rccb are protected against overload and that diversity of the final circuits shall not be solely used.Total MCB rating of 88A on a 63A RCD. Is this still allowed?
A nonsense I agree, but some manufacturers are adamant this is no longer permitted.
Edit: What rating is the cutout fuse?