Discuss Has this consumer unit been installed correctly? in the UK Electrical Forum area at ElectriciansForums.net
That's why Hager is fitting only 100A RCD's in their consumer units now.The regulations now require that the main switch and rccb are protected against overload and that diversity of the final circuits shall not be solely used.
Manufacturers instructions should be followed.
The primary ocpd could be 60/63 amps so it would be acceptable, then again it could be 80/100
Total MCB rating of 88A on a 63A RCD. Is this still allowed?
A nonsense I agree, but some manufacturers are adamant this is no longer permitted.
Edit: What rating is the cutout fuse?
Is that your before or after photograph?Just to keep things interesting... check this out what I managed to find on close inspection.
View attachment 49490
A right Bogger's muddle. awful, a Plumber was he? cus he aint no Electrician, if he says he is, he want's to give up, and flog his tools, any certificates issued? if so I would love to look at them, was he a member of one of the CPSchemes?Hello,
Had a sparky install a new consumer unit, has it been done correctly. Bare in mind the chap cut corners on other bits of work he was contracted to do.
View attachment 49367
Its always a sorry tale when work has to be redone and paid for a second time
Poor standards even reflect negatively on the vast majority who do good work and are honest tradesmen
A couple of hundred too cheap I reckon.Sounds a bit cheap to me, but not ridiculously so.