T

Tucosweep

Hello guys,
I am wiring a shower and need to know if I have got this right?

It is a 8.5kw shower with a 15m cable run in mini trunking.

I have selected a 40A mcb, 6mm cable with a current capacity of 38A, and the volt drop is just inside.

BUT, after looking in the electricians guide to the wiring regs it says I must have 10mm cable for a shower rated between 7.5-9.5kw,

can I proceed with the 6mm cable?

kind regards
Grant
 
your CCC at 38A would require a 32A MCB ( In < Iz ). a 32A MCB ain't gonna trip on 8.5kW for the length of time the shower is on. calc. current is 36A but i bet a clamp meter will show a bit less.
 
Hello guys,
I am wiring a shower and need to know if I have got this right?

It is a 8.5kw shower with a 15m cable run in mini trunking.

I have selected a 40A mcb, 6mm cable with a current capacity of 38A, and the volt drop is just inside.

BUT, after looking in the electricians guide to the wiring regs it says I must have 10mm cable for a shower rated between 7.5-9.5kw,

can I proceed with the 6mm cable?

kind regards
Grant

Grant, surely you know that the MCB is to protect the cable so if the cable rating is 38A and the MCB is 40A which is going to fail first?
 
Has I understand it (8.5kw @ 240) that's (7.8kw @ 230) is says that on the box.......now 7800/230 = 34 amps which mean you need a 40amp mcb.....as for cable you need higher then 40 because that's the fuse size. now cable 6mm clipped direct method C is 46a which is fine but in trunking method B (your way) is 38a just not enough so 10mm is required.........as for the guide its always suggested 10mm because people will swap the unit from 8.5kw to 10.5kw when it comes to replacing it. So 10mm covers all angles
 
Hi,
Yes, I have been a bit slow on this one.
i have stupidly bought 6mm cable, is there a way round it?
can I strip the cores into singles to give me a CCC of 41A then sleeve the earth?
kind regards
Grant
 
strangely enough there is no reference method B quoted for flat T/E cable. IMO.6mm T/E will happily run all day long at 40+A in mini trunking, so I'd
go with a 40A MCB up to 9KW. tin hat on boys.
 
Grant, are you actually an electrician? Also, this work is notifiable under part P (either before you commence work if not registered, or after completion if you are).
I only bring up these points due to the fact that you bought the 6mm cable without being sure, and stated that you were considering running cable you rated at 38A with 40A protection.
 
if you use 10mm then those nice men in the disposable white overalls can come and smother it in 12" of itchy-poo crap wthout it overheating and setting the attic on fire. one day they might even manufacture pull switches that can accomodate 10mm cable and still get the outer sheath inside the box.
 
if you use 10mm then those nice men in the disposable white overalls can come and smother it in 12" of itchy-poo crap wthout it overheating and setting the attic on fire. one day they might even manufacture pull switches that can accomodate 10mm cable and still get the outer sheath inside the box.

Crabtree 50A pull switch?
 
one day they might even manufacture pull switches that can accomodate 10mm cable and still get the outer sheath inside the box.

You not used the Crabtree (or much cheaper Scolmore identi-copy) 50A pull switches, then? 10mm no trouble at all with a bit of sheath inside.
 
You not used the Crabtree (or much cheaper Scolmore identi-copy) 50A pull switches, then? 10mm no trouble at all with a bit of sheath inside.

Sunday = slow typing
 

Reply to Have I got this right? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
123
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
910
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
There are two reasons for a fuse/mcb they are: 1) fault conditions - which must exist always, and be capable of operating for all points on the...
Replies
4
Views
1K
  • Question
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
Replies
3
Views
744

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top