I've been in an ongoing debate regarding earthing of a control transformer and i'd like some other opinions.

690 primary, 120v secondary supplying control circuits (contactors/DC convertors etc), the neutral is tied to earth - My issue is the location that it is tied to Earth.

As far as I know the difference between a TN-S and a TN-C-S system is whether or not the neutral is connected to 'ground' at the source or further down the line.

60079-14 - 6.3.2 TN type of system earthing If a type of system earthing TN is used, it shall be type TN-S (with separate neutral N and protective conductor PE) in the hazardous area, i.e. the neutral and the protective conductor shall not be connected together, or combined in a single conductor, in the hazardous area. At any point of transition from TN-C to TN-S, the protective conductor shall be connected to the equipotential bonding system in the non-hazardous area.

Please see attached photo; The proposed design shows the point where the neutral is tied to earth (circled in blue) - this makes the highlighted section the 'C' in a TN-C-S system.

To create a TN-S system it would need to be where it is marked Red (taken directly off the transformer)

Also the highlighted cable is a line bushing from an Exd enclosure (which houses the transformer) to a close coupled Exe enclosure so this bushing cable would be combining the neutral and protective conductor.

Any thoughts agreeing/disagreeing? I can't seem to budge some peoples stance on it and to me it's black and white.

Cheers.

It’s fairly standard practice to be honest
 
I've been in an ongoing debate regarding earthing of a control transformer and i'd like some other opinions.

690 primary, 120v secondary supplying control circuits (contactors/DC convertors etc), the neutral is tied to earth - My issue is the location that it is tied to Earth.

As far as I know the difference between a TN-S and a TN-C-S system is whether or not the neutral is connected to 'ground' at the source or further down the line.

60079-14 - 6.3.2 TN type of system earthing If a type of system earthing TN is used, it shall be type TN-S (with separate neutral N and protective conductor PE) in the hazardous area, i.e. the neutral and the protective conductor shall not be connected together, or combined in a single conductor, in the hazardous area. At any point of transition from TN-C to TN-S, the protective conductor shall be connected to the equipotential bonding system in the non-hazardous area.

Please see attached photo; The proposed design shows the point where the neutral is tied to earth (circled in blue) - this makes the highlighted section the 'C' in a TN-C-S system.

To create a TN-S system it would need to be where it is marked Red (taken directly off the transformer)

Also the highlighted cable is a line bushing from an Exd enclosure (which houses the transformer) to a close coupled Exe enclosure so this bushing cable would be combining the neutral and protective conductor.

Any thoughts agreeing/disagreeing? I can't seem to budge some peoples stance on it and to me it's black and white.

Cheers.
I don’t see a problem by bonding where you have circled in red. I have to agree with you why bond it again
 
Well the most immediate problem I read is that you are using an Exe enclosure, with a supply that is not rated Exe.

So right off the bat this installation isn't going to comply.

At this voltage and power availability, Exd is the option you should be looking at.
 

Reply to Hazardous areas - control voltage transformer earthing - in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
786
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Replies
14
Views
660
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top