B
bigbaddave
Right here goes, I have a large domestic house in Yorkshire which I've attended due to tripping RCD. Originally a dual RCD and I'm the third spark to look at this. Previous spark is a guy I work with and I know it's had a lot of time spent on it.
The side that was originally tripping had been swapped to individual RCBOS and the circuit that trips is upstairs lights however will only trip when a large current is pulled (kettle, toaster) on the kitchen sockets and this circuit is on the other side of the split loads board covered by the one RCD.
the tripping does not continue when the CPC is removed from the earth bar (upstairs lights) all class 2 fittings.
test results - IR global for DB (N-CPC ) 10.6 meg CPC - Live 15.7 meg L-N 21meg
IR between two n bars 999meg
IR between lives all 999 meg
RCD tests fine and been replaced along with RCBO
I'm due to go back but the contractor I work for is suggesting we just rewire the circuits we are having problems with as the cost of testing and time it's costing the company money not having the install working as it should. I Hate being beat.
The side that was originally tripping had been swapped to individual RCBOS and the circuit that trips is upstairs lights however will only trip when a large current is pulled (kettle, toaster) on the kitchen sockets and this circuit is on the other side of the split loads board covered by the one RCD.
the tripping does not continue when the CPC is removed from the earth bar (upstairs lights) all class 2 fittings.
test results - IR global for DB (N-CPC ) 10.6 meg CPC - Live 15.7 meg L-N 21meg
IR between two n bars 999meg
IR between lives all 999 meg
RCD tests fine and been replaced along with RCBO
I'm due to go back but the contractor I work for is suggesting we just rewire the circuits we are having problems with as the cost of testing and time it's costing the company money not having the install working as it should. I Hate being beat.