Head went funny.... Reverse polarity showed up and still after swapping cables ? | on ElectriciansForums

Discuss Head went funny.... Reverse polarity showed up and still after swapping cables ? in the UK Electrical Forum area at ElectriciansForums.net

LukeD

-
Nearly Esteemed
Arms
Supporter
Joined
Jan 7, 2011
Messages
1,835
Reaction score
1,470
Maybe lack of coffee etc ! Voltage also dropped to 140 for a bit . New ring . wired up correctly but indicated "reverse " . Could not be possible . Then tested other way and same thing ! Its a luxury apartment and only in there fitting longe plates. Building sparks arrived and fiddled in Consumer and it all came back to life. My remit did not allow me to open Consumer
 
My best guess as follows:

Dead tests all passed fine.
Someone then manages to connect L+N backwards at consumer unit. More likely in an RCBO hence earlier question.
Circuit is energised for live tests.
Plug in and Zs test or RCD test will upset tester as Live to Earth is 0v and N to Earth is 230v. Most makes will show a warning lamp, or not light one of two orange lamps.
While removing either N or Earth some testers will show half supply voltage, maybe that explains that bit.

What I haven't worked out yet is your comment "tested other way and same happened". Did you swap two test leads over? If so was it definitely L and N you swapped?
 
My best guess as follows:

Dead tests all passed fine.
Someone then manages to connect L+N backwards at consumer unit. More likely in an RCBO hence earlier question.
Circuit is energised for live tests.
Plug in and Zs test or RCD test will upset tester as Live to Earth is 0v and N to Earth is 230v. Most makes will show a warning lamp, or not light one of two orange lamps.
While removing either N or Earth some testers will show half supply voltage, maybe that explains that bit.

What I haven't worked out yet is your comment "tested other way and same happened". Did you swap two test leads over? If so was it definitely L and N you swapped?
THis would make sense. I was there only to fit some custom lounge plates . Was told not to touch CB etc by property manager as The client is still "buying" the property ! I swapped L & N and still got the initial error message
 

Reply to Head went funny.... Reverse polarity showed up and still after swapping cables ? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
814
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
873

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top