T
Tosh
Hey folks looking for a second opinion on this one, was carrying out an eicr on an car dealership it department , all going well just the usuall cracked sockets blind grommets missing from things etc . Got to one board that feeds a lot of it computers and there was obvious heat from the DB cover before I removed it , there was heat in the RCBOs and associated cables that was easy noticed , I wouldn't have expected such heat as there's no load in the computers , any ideas on this one:bulb2:
Did you check what current was being drawn by the different cables? 70 degrees is pretty warm :)
No my van was a good bit away with the clamp meter in it, but didn't think there was enough computers there to warrent the heat output , was just wondering if any one else has had this in an it department
No I have not tested the board as the person ordering the work is on holiday and I want clarification as too what is a limitation on the board as I cannot kill power to most circuits as the board feed offices that deal with it customer services etcNd there is also a board which just feeds the server equipment which I have meant to test but the place is open 24/7 so I want a method statement off the person ordering the work to tell me when I can issolate supies , it was only when removing the DB cover to do a dead test on a sub main circuit I felt the heat , was just looking for some advice
How did you do a dead test on the sub main without isolating the board.
It was it was DB fed from the board that had the heat in I that is was testing . Ie a 63 amp 3 phase mcb feeding a DB that I was testing so i could issolate the DB that was fed via the DB which had heat in it
The heat dissipated by an MCB or RCBO depends on how near its rating it is running. It is not just the total load that is of interest in DB self-heating but what size circuits and breakers are carrying it.
I would also check the tightness of all the connections in the main distribution board. Oh, and when your next there, take your amp clamp with you. Totally pointless having test equipment if you're just going to leave it in the van!!
Reminds me of a small control panel I built for control of 5 radiant heaters, total capacity was 16.5KW, I mounted the thermostat to control the heaters inside the panel..... bad idea. The heat from just the cables and contactors raised the temp inside quite a lot really. Felt like a small heater in itself. Anyway, moved the thermostat to outside the panel after that. Point being when stuff is running at high current for periods it does generate heat. whether its a concern or not can only be done by testing against the limits of the equipment installed. I often come across warm equipment. I only get really concerned if I cannot keep my hand on it.
Use a temp sensor and see if you can pin-point the offending circuit, if there is one. then take it from there.
Heat felt in cables
Thread Tags
Tosh,
itselectric,