I've got an outdoor heating circuit that I'm trying to fault find.

There are four heaters under a parasol each rated at 1.5kW that are tripping two MCBs in series. One is on the main board the other is in a separate unit dedicated to the outdoor circuit. When the heaters are cold if all four heaters are plugged in then both Mcbs trip instantly. If only two are plugged in it starts and then you can plug the other two in and there's no problem. Then when it times out if it's switched back on immediately then they come on without a problem.

Both MCBs are B types BSEN 60898 hager and MK.
There is no problem with IR
The measured resistance of a heater when cold is 4 ohms
This would give each one a starting current of 57.5 A
So the four together would have a startup current of 230 A or 52 kW

My first thought was to change the MCBs to C or D types but on reflection of these figures that would just result in a tripped main switch. I am thinking of some sort of soft start current control option but I haven't used one before and I'm not sure if that's the best solution.

Apparently it used to work, but I don't see how.

All thoughts welcome.
 
Right well this is the next thing. The current for the heaters is switched through a contactor. As I said before, I haven't used one of these soft start units before, but from what I can see they appear to work through the switch. I assume they work by having a high resistance added to the circuit which would decrease either though a timer or some temperature control thereby reducing the start up current but not interfering with normal operation. If that is the case then having on at the switch in this case wouldn't work because that would only affect the switching current and not the current which goes through the devices when the contactor switches on the load current.

Is there a soft start contactor or should I just recommend that they change their heaters, rewiring their circuit would be the most expensive option.

Oh if I put a Cs or Ds in it will blow the main switch
 
The theory is quite simple. Some conductors have higher resistances when hot. For that reason some heaters will draw more current as they are starting up. I would have expected an electrician to know this.
 

Reply to Heater start up currents in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
74
  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
389
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
352

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
I've seen a few posts here which tend to suggest that wiring in a motorhome (or caravan) wouldn't be subject to normal inspection rules, but even...
Replies
0
Views
327

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top