Heating element earth trip | on ElectriciansForums
Discuss Heating element earth trip in the UK Electrical Forum area at ElectriciansForums.net
Shropshire
Hi,
Can a heating elements resistance to earth depend on its temperature? As I have one here that trips the RCD but when checking the resistance cold there is around 1.5M ohm-7M ohm to earth which shouldn't trip a 30mA RCD. Putting pressure on the element doesn't change it and there aren't any obvious burnt spots where arcing could have occurred.
Could the element still be faulty but only when it heats up? This is from a Kenwood bread maker. Between the element terminals it reads about 90 ohms so it appears to be intact, maybe the elements resistance wire only makes contact with the outside when it heats up.
Thanks.
what he said.^^^^^. try heating it up , either till the RCD trips, or temp. bupass the RCD then megger it. go to 1000V if necessary. only other way is to swap the element then see if the fault is cured.
Another common problem is that any moisture dispersed through the insulant can condense at the cold ends when the element is first heated. You get a very sudden drop in insulation resistance that slowly rises again as the moisture is driven off. But seeing as it is the bread that should rise and not the IR, sounds like you need a new one.
Black iron heating elements a well known for causing RCDs to trip.
Because of this, I don't like to use RCDs to protect cookers or storage heaters.
Often the fault can be sorted just by re-setting the RCD a few times.
In some instances (especially if the element has not been used for some time), it may be necessary to by pass the RCD, until the element has dried out.
Another option is to use an IR tester, hold the button down until the moisture is boiled off by the voltage used by the tester (the reading should improve as the button is held down).
If the IR is a problem when it heats up you can try baking the element at 300 Celsius in an oven for 12-24hrs. If there's a silicon seal around the ends of the tube remove them first and reseal after baking. If that doesn't improve the IR then I'd replace it with a new one.
...... bupass the RCD then megger it. go to 1000V if necessary .....
...... you need to use a megga for insulation
Can we use the correct terminology gentlemen, as intimated below by Mr Spinlondon. There are DIY users on the forum who can be easily confused by such statements ...... not to mention the trainees and 'old' sweats :biggrin:
.......Another option is to use an IR tester ......
It'll be cheaper to go and buy a new element than to run an oven at 300C for 24 hours!! lol!!
You're probably right with the price of electricity nowadays we tend to work with batches of elements rather than a single tube. We also use an oxy-acetelene torch sometimes as a short cut but it's a bit hit and miss.
My mum gets very cross,when i fix her bread-maker,as the rubber tyres on my oxy/acetylene trolley,leave marks on the kitchen floor...:conehead:
I hope you never use the term 'Hoover' then, or 'Tannoy'. Daz
Reply to Heating element earth trip in the UK Electrical Forum area at ElectriciansForums.net
Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
I fitted a Mem MR30 Pod and MCB, about ÂŁ75 for both.