bobby101

hi all could somebody tell me if there is a diffrent requirement for the height of sockets and switches on a commercial property or does the same regulation height for domestic properties apply if poss could someone tell me where to gain a factsheet on this thanks in advance..
 
Regulation 553.1.6 covers sockets and as in domestic there is no specified heights as it is all down to wether the height will damge the flexible cord

In domestic new builds there are building regulations and these are covered in the OSG pg 161 section 8.6. Mostly on commercial or industrial the designer will specify heights and he may have to take into account some local or other regualtions appertaining to the type of enviroment.
 
Hi there, dont know if this will help, I wired 10 individual units within a block for the local council and they stipulated the DDA to me about socket/switch heights and the such.
 
Last edited:
It depends who's going to be using them - part M was introduced to make things more accessible for persons with restricted reach, which may not be applicable if for example the IT equipment is managed exclusively by the IT department (desktop support can be expected to be in reasonable physical condition) so IT equipment could be plugged into a floor box.
Provision should be made for electrical equipment for use by those with restricted reach, eg a socket should be accessible at reasonable height for someone to be able to plug in a mobile phone charger.
 
Thought some measurements might be useful. Basically the rule in domestic premises is anywhere between 450mm and upto 1200mm from finished floor level. As far as I know there is no specific requirement in commercial premises, but be aware that there maybe disabled users who need to reach lights switches etc.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
heights of sockets and switches
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
5
Unsolved
--

Advert

Thread statistics

Created
bobby101,
Last reply from
scotsparky,
Replies
5
Views
7,429

Advert

Back
Top