Hello all I have recently started working for myself and allwas ok until one of my customers called
Basically I upgraded an old Consumer unit to a 16 duel RCDwith a Vphase system integrated on it
All tests where done before leaving and signing off
Now the tumble dryer is tripping the rcd the dryer is new soI doubt it is faulty or wet inside
The rcd times are (fine I think)
1 times 29.3 @ 0
1 times 19. 1 @ 180
5 times 8.59 @ 0
5 times 15.0 @ 180
Ramp is 48 @ 0 & 48 @ 180
The only option I have is to move the ring off the rcd but Ido not want to do this
Your help is appreciated