I am preparing 302 written test.
One thing is confusing.
8kw 230 v cooker using T&E pvc cable directly clipped. the circuit is prtected by BSEN 60898 type B circuit breaker.
the run covers 18m. the ambient tempurature is 35 C.
With this given condition, I need to cable size, design current, fuse rating etc.
I did get the answers.
the design current is 34.8A(Ib)
the rating of circuit breaker is 40A(In)
minimum size of cable is 6 mm2
However, one of questions is that "the eath fault loop impedance Zs is 1.12 ohm; does the circuit comply with Bs7671?
I got Zs(max) value 1.15 ohm (from table 41.3 of bs7671), and the measure Zs value is 1.12
Does it complies? The given answer is 'YES'
But I think I need to apply the rule of thumb : Zs> 0.8 X Zs(measured).
If I apply the rule of thumb, then it doesn't comply.
What is your opinion?
I hope I made myself clear for the question.
Thanks
One thing is confusing.
8kw 230 v cooker using T&E pvc cable directly clipped. the circuit is prtected by BSEN 60898 type B circuit breaker.
the run covers 18m. the ambient tempurature is 35 C.
With this given condition, I need to cable size, design current, fuse rating etc.
I did get the answers.
the design current is 34.8A(Ib)
the rating of circuit breaker is 40A(In)
minimum size of cable is 6 mm2
However, one of questions is that "the eath fault loop impedance Zs is 1.12 ohm; does the circuit comply with Bs7671?
I got Zs(max) value 1.15 ohm (from table 41.3 of bs7671), and the measure Zs value is 1.12
Does it complies? The given answer is 'YES'
But I think I need to apply the rule of thumb : Zs> 0.8 X Zs(measured).
If I apply the rule of thumb, then it doesn't comply.
What is your opinion?
I hope I made myself clear for the question.
Thanks