Hi guys,
Bit stumped here.
Have an rccb split load Crabtree star breaker... Which is tripping with any load put on it. The only circuit which is on this rccb is my new 20a radial for sockets. I've done my cont at .46 my insulation passes at greater than 299. Did an Rcd test which passes .. Did a ramp test also and trips at 27mA
Checked the nuetral tails into the rccb they are ok... Am I missing somthing obvious?? Another thing tried doing a zs on no trip but it does trip. Tried swapping the rccb but same issue.
Thank you for help in advance
Bit stumped here.
Have an rccb split load Crabtree star breaker... Which is tripping with any load put on it. The only circuit which is on this rccb is my new 20a radial for sockets. I've done my cont at .46 my insulation passes at greater than 299. Did an Rcd test which passes .. Did a ramp test also and trips at 27mA
Checked the nuetral tails into the rccb they are ok... Am I missing somthing obvious?? Another thing tried doing a zs on no trip but it does trip. Tried swapping the rccb but same issue.
Thank you for help in advance