This problem solving was on Virtual Scenarios (Ring Final Circuit) Getting Value of R1+R2
2.5mm and 1.5mm size cable used.
1st From the C.U. values of following connection
L to L =0.27
N to N =0.27
CPC to CPC =0.45
2nd from the C.U cross the outgoing L to the incoming N and vice versa
Measure between L and N at each socket outlet.
socket 1 = 0.16
socket 2 = 0.16
socket 3 = 0.17
socket 4 = 0.18
socket 5 = 0.46
3rd from the C.U cross the outgoing L to the incoming CPC and vice versa
Measure between L and CPC at each socket outlet.
socket 1 = 0.73
socket 2 = 0.73
socket 3 = 0.75
socket 4 = 0.74
socket 5 = 1.2
I'm confused which of the value of R1+R2 to be recorded?
Is there something to be calculated to get the value of R1+R2?
With those readings I would say that socket 5 is a spur - so take it off the wall and check it has only 1 cable - if it has 2 cables it may still be a spur with a spur off a spur OR be a dodgy socket, so try the readings off the cables.
hope this helps
Ps you record the highest reading
2.5mm+1.5mm T&E. r1 and rn should have the same value of resistance measured end to end (within 0.05 of each other). r2 is obviously going to be of a higher value of resistance than r1 or rn due to the CPC being of a smaller CSA (times the value of r1 by 1.67). The value of r1 and the value r2 added together and then divided by four will give you your R1+R2 value.
Reply to Help me to Understand to get value of R1+R2 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net