malaysia
Ac power supply 440V
Inverter - Input 380-480V 50/60hz 11.2A
Output 0-480V 8.5A 6.8kva 3.7Kw
3 phase motor- 2.2kW 50Hz
Should i use delta or star connection?
newguytoelectricity
it's quite likelythat a motor that size will be 415V 3 phase star and 230V 3 phase delta. if so wiring it in delta will fry the motor. to be safe, I advise wiring in star config. unless the rating plate says otherwise.
You have a VSD with 400 3ph input and 400 3ph output, as long as your motor has a 400v option which I suspect it almost certainly will then there is no real advantage to setting the VSD up as though it was running a 230v 3ph.
Reply to Help me with inverter vfd to 3 phase motor in the Electrical Engineering Chat area at ElectriciansForums.net
Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Hi, Thanks for that, you learn something new almost every day! Regards Griffey