If I have motor with frequency 50HZ, 415V and I want to operate it on frequency 60HZ, 415V



Or

If I have motor with frequency 60HZ, 415V and I want to operate it on frequency 50HZ, 415V

What will be the effect of the motor?
 
Last edited by a moderator:
The function of a electrical motor or transformer is dependent on the Hertz or cycles of the alternating voltage or current. This means that a motor or transformer would not function if the electrical voltage was not alternating.
Basically a motor or transformer is made by a manufacturer for a specific Hertz or cycles, so either for 50 or for 60 Hz.
This is mentioned on the nameplate of the equipment.
Sometimes it mentions both Hertz 50 and 60, but this is only for small (low wattage) motors and small transformers.
Larger motors or transformers are only made for a specific amount of Hertz, so either 50 or 60.

What happens if you connect a 60 Hertz motor to a 50 Hertz mains:


The motor turns 17% slower
The internal current goes up by 17%
The power (watt) goes down with 17 %
The mechanical cooling is less, because of 17% less turns
The result is a higher current, then designed by the manufacturer and the insulation of the electrical wiring deteriorate much quicker, which after sometime results in a burn-out.
 
If you use inverters which chop the frequency signal on a motor to control speed you can exceed its normal operating frequency in the setting to achieve a faster speed but the result is a loss of torque and go too high you can get a stall effect just like trying to set off in 5th gear in your car.
 
If you are trying to get more duty out of the a motor ie fan or pump because its under sized then upping the hertz on the inverter is not the way the motor will not last long it will burn out. what ever you do get it in writing off the motor manufacturer

i done a job in January where the AHU fan motor was off its curve and they were not getting the duty. due to the fan being under sized (the consultant had F***ed up) The motor manufacturer advised the motors could do 55Hz this was still not good enough and eventually a figure of 74Hz was used. The motors did not last 6 months.
 

Reply to Help: Motor and frequency in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
pretty sure from memory they are indeed designed to work on both frequency's, Best check with Schneider but I think they will work on 60 HZ
Replies
4
Views
536
That sounds to be more of a control issue rather that a motor issue Are all the limit switches working properly and not sticking occassionally
Replies
1
Views
320
Hi, Thanks for that, you learn something new almost every day! Regards Griffey
Replies
5
Views
1K
Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
306
  • Question
The closest modern equivalent are the EV chargers that use a rod to detect open-PEN faults on TN-C-S supplies. Most RCD will trip on the current...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks