hello there your expertise please
Basically recieved a job from a client that rents out propertys the client has had the council complete a EICR and they have found x2 ring mains have the following faults:
circuit 1:no continuity lives (readings-RN=1.33)
circuit 2: no continuity neutral (readings-R1= 1.28)
the fuseboard also needs to be replaced but i have told the customer before we change the board for new 17th edition consumer unit we need to correct these faults i was just wondering what you would do?
1) try find fault hourly rate take all socket fronts off and inter connect cables at board and test each socket until find break
2) change mcb in 16a and turn into radials
or recommend rewire sockets please note he doesnt want to spend alot (useual story) as hes just renting the place out
PS insulation ressistance readings are fine
thanks very much