Help needed with Ring(s) problem | on ElectriciansForums
Discuss Help needed with Ring(s) problem in the Australia area at ElectriciansForums.net
L
LlandrilloSpark
Fellas could do with your valued opinion on the following
Bungalow, 40 year old wiring, TNCS, two 30a ring finals for socket outlets but i fear lots of diy additions, IR reading of 0.01 Meg Ohm Line-Earth on both legs of both rings, also i think the rings are connected as only 25Ohm resistance between line conductors from each ring.
The install has worked perfectly and not blown the 3036's i 40 years.
Any thoughts?
Cheers
Ummm... first thought is that you need to find the 25 Ohm connecting between the two rings first because that will be meaning that the 0.1 MOhm IR result appears in both places. (It's probably only an IR fault on one of the rings, but appears on both because they are linked together.)
Then the usual things... everything unplugged? split the rings and test each half, etc...
Cheers lads
TV ARIEL BOOSTER!, somebody mentioned it, well this is strange, I unplugged appliances one at a time just to eliminate any faulty ones, the last one was a very old tv ariel booster, when i unplugged it the fault went, i plugged it back in the fault was there, i checked again 3 times and i thought i'd solved the problem on at least on circuit, but after being energised the fault returned!
Im a bit stuck but customer is willing to chuck 4-5 hours at it tomorrow and i really want to solve it.
r.e Neutral and Earth IR's both over 25 Meg
Why did you not unplug everything before you carried out IR test???
Schoolboy error :p
Edit: if it were me testing id be stripped each point down and testing between, draw it out too, its a long arsed process but will pinpoint your fault
Reply to Help needed with Ring(s) problem in the Australia area at ElectriciansForums.net
  • exceeding voltage drop
    The cable is way undersized. If the voltage drop is detrimental to the installation I would make...
  • TT advise
    OK My take on the precautions to implement when omitting an up front RCD on a TT system. Tails...
  • SIL vs ATEX
    Good morning all, I have a question for those who are CompEx and SIL aware - I have various Ex...