I have been called to a job by a builder after his electrician walked out.
The client wants a new kitchen installation and after testing the old circuits I have informed him that they are all compromised and need to be replaced.
The current board has no RCD protection and I have informed them that this will need replacement in the future.I do not want to replace the main board yet as based on the kit circuits this would be a can of worms and there is some discusion between builder and client over who is resposible for costs.
In the meantime I have installed a sub-board with a 83A 30ma RCD as main incomer supplied through a Henley block for the kitcen circuits from 100 amp Main fuseI intend to rewire for just the kichen.
Because of the layout of the kitchen and the high spec of the the fitted appliances I have decided to install 2x 4mm radials for the small number of sockets reqired (10).
The hob is 6kw so I am using 6mm with 32A mcb.
The oven circuit has 3 ovens and a built in coffee machine The total wattage of 9850w -43 Amps
I have decided to use 16mm T&E with 50 Amp mcb as max demand on 10 mm is 40Amp.All sockets and ccbs rated accordingly.
I have informed the client that his new board Has allowing for diversity max demand of 85 amps and his old board has 80 amps and told him to contact DNO to confirm the supply setup is satisfactory.
He has also asked me to rewire the lighting circuit.As this would also be connected to the new board increasing the demand .
Firstly.Have I made any serious errors or ommisions
Secondly should I upgrade the RCD to 100Amp 30ma
Thanks for any help or advise
The client wants a new kitchen installation and after testing the old circuits I have informed him that they are all compromised and need to be replaced.
The current board has no RCD protection and I have informed them that this will need replacement in the future.I do not want to replace the main board yet as based on the kit circuits this would be a can of worms and there is some discusion between builder and client over who is resposible for costs.
In the meantime I have installed a sub-board with a 83A 30ma RCD as main incomer supplied through a Henley block for the kitcen circuits from 100 amp Main fuseI intend to rewire for just the kichen.
Because of the layout of the kitchen and the high spec of the the fitted appliances I have decided to install 2x 4mm radials for the small number of sockets reqired (10).
The hob is 6kw so I am using 6mm with 32A mcb.
The oven circuit has 3 ovens and a built in coffee machine The total wattage of 9850w -43 Amps
I have decided to use 16mm T&E with 50 Amp mcb as max demand on 10 mm is 40Amp.All sockets and ccbs rated accordingly.
I have informed the client that his new board Has allowing for diversity max demand of 85 amps and his old board has 80 amps and told him to contact DNO to confirm the supply setup is satisfactory.
He has also asked me to rewire the lighting circuit.As this would also be connected to the new board increasing the demand .
Firstly.Have I made any serious errors or ommisions
Secondly should I upgrade the RCD to 100Amp 30ma
Thanks for any help or advise