hi i have been called to a house with the rcd tripping out found out side sockets causing some faults so i removed that now the rcd still trips out even if i turn all the connecting mcbs off any idea what would cause this.

o i also tested the kitchen ring and found on a end to end test the live reading was 97.0 ohms and the neutral was around 0.60 ish also any ideas i would really appreciate help.

cheers mike
 
hi i have been called to a house with the rcd tripping out found out side sockets causing some faults so i removed that now the rcd still trips out even if i turn all the connecting mcbs off any idea what would cause this.

o i also tested the kitchen ring and found on a end to end test the live reading was 97.0 ohms and the neutral was around 0.60 ish also any ideas i would really appreciate help.

cheers mike


what type of supply tt?, rcd fault is normally between neutral-earth,so turning off mcb will not cure problem quick fix- divide consumer unit neutrals say 1st 4 circuits disconnect,try to reset,no good then replace then other 4 circuits,keep dividing until you find affected circuit,disconnect all current using equiptment and megger n-e.are the cables to the outside sockets ok not got corroded or water etc.

kitchen ring sounds like corrosion on conductor do r1 & r2 from cu to mid point on ring then remove socket and seperate ring main faults are time consuming but sometimes you may get it straight away,depends how it was wired(all dead testing as you know)hope this helps
 
hi mate yes it helps it is a TNCS system but it has even tripped when i have turned all the mcbs off from the rcd side and it still tripped any idea
 
hi mate yes it helps it is a TNCS system but it has even tripped when i have turned all the mcbs off from the rcd side and it still tripped any idea


remember it is probably n-e fault,so turning off mcbs will not alwats cure it,is the rcd faulty?do you have a tester to do a 1/2 test on say 30ma for nuisance trip,
 
RCD tripping with all MCBs off either an earth fault or perhaps you have a loose connection causing an imbalance between live and neutral. Have you checked your voltage at the RCD


Chris
 

Reply to help please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
856
  • Question
Live wires under floorboards? any years ago, when my daughter was just a crawling stage, we were having a new carpet fitted in an upstairs room...
Replies
9
Views
979

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top