Is there any way the garage and summer house can be supplied form the existing house DB to cut down on the demand of the extension DB as you say there are 2 spare ways in it???
Not really would be hell of a run, Already moved a 1 x ring and 1 x lighting circuit on to there from extension to get my figures down.
I'm wondering though about the 2 x 20amp supplies to the garage and summer house. Will these be feeding CU in those locations? as I'm sure that supply will logically be divided into lights and power.
Thats right they will be feeding a 2way CU in each location. And Both will be TT as existing property being upgraded to PME. Summerhouse is 25m away and will have 1 x 15a radial running from CU supplying single socket and garage which is 10m away will have 1 x 15a radial supplying 1 x single socket and FCU to supply light.
Right think I've got it under control now, panic over....
Spoke to customer informed them that there is possibility of that there existing 100a supply may not be adequate (informed them of worst case scenerio and what may be involved etc..), they are going to have a word with DNO when they come out to upgrade the PME and see what calcs they apply and if it is required.
Got my figures sorted out now:
Submain to cu 1: 10mm 3c SWA to feed : hob,ovens,immersion = 50a max after diversity (30m run ref D)
Submain to cu 2: 16mm 3c SWA to feed : ring,lights,s.house,garage = 69a max after diversity (30m run ref D)
And my be able to get runs down to 25m....
Thanks for all your help,
Sy