hi al,l newbee here and this is my first post.


now the question i am about to ask may sound dumb, but here goes

we all know that 2.5mm t/e cable is use for ring mains, but how do we prove that. a question on a course work i am doing requires a ring main circuit to be designed from stratch. this is how far i have got (now no laughing)

i have given 7200W as a maximum for the ring main

so Ib = P / U
= 31.3 Amps
In = 32 Amp RCD

It = In / CFs
It = 32 / 0.85 x 0.88 (thermal and grouping)
It = 32 / 0.748
It = 42 Amps

now 2.5mm takes 27Amps max when clipped direct, do i devide the calc by two

ie It = 42 / 2 = 21Amps (so the 2.5mm t/e can be used)


please help

the man (pete)
 
Ring circuits covered by 433.1.5. For a ring circuit each branch should have a current carrying capability of 20A, if the load current in any part of the circuit is unlikely to exceed for long periods the current-carrying capacity of the cable.

What you need to do is take the 27A for 2.5mm and apply the thermal and grouping effects to that, and I believe that will be greater than the required 20A.

Thats my 2p worth anyway!
 

Reply to help please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
782
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

Generally it would depend on the circumstances whether the armour is earthed both ends or not, and not just dependent on whether it's 2 or 3 core...
Replies
9
Views
357
And fully tested it with an MFT obviously
Replies
9
Views
705

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top