Help putting power to a shed!! | on ElectriciansForums

Discuss Help putting power to a shed!! in the Australia area at ElectriciansForums.net

E

eskimo39

Hi this will be my first job for myself since qualifying and just would like a little assurance if possible.

A friend has a garden shed 40 meters from his house and would like sockets and lighting putting in. I am thinking 6mm2 SWA 3 core going from his original house CU (protected by rcd and 40a mcb) to a Wylex 2way Garage Consumer with RCD in the shed. Inside the shed 3 x metal clad double sockets on a 2.5mm ring with 20a MCB and a couple of lights on 1.5mm protected by 6a mcb.

I have done a few calculations and estimate load to be approx 8kw (3 sockets at 13a with voltage at 230v giving 8280w) Also on the length of cable I estimate voltdrop to be 9 volts.

Would this be o.k???

In the garage there will be a fridge on one socket, a freezer on another and one spare for lawnmover/hedgetrimmer etc.

Any suggestions/alterations would be greatly appreciated.
 
Hi this will be my first job for myself since qualifying and just would like a little assurance if possible.

A friend has a garden shed 40 meters from his house and would like sockets and lighting putting in. I am thinking 6mm2 SWA 3 core going from his original house CU (protected by rcd and 40a mcb) to a Wylex 2way Garage Consumer with RCD in the shed. Inside the shed 3 x metal clad double sockets on a 2.5mm ring with 20a MCB and a couple of lights on 1.5mm protected by 6a mcb.

I have done a few calculations and estimate load to be approx 8kw (3 sockets at 13a with voltage at 230v giving 8280w) Also on the length of cable I estimate voltdrop to be 9 volts.

Would this be o.k???

In the garage there will be a fridge on one socket, a freezer on another and one spare for lawnmover/hedgetrimmer etc.

Any suggestions/alterations would be greatly appreciated.
Sounds fine mate,but if you are protecting the circuit with an RCD at the main CU and the shed,then both RCD's will trip.Can you not put the shed circuit on the non RCD side of the board,if the board is suitable.
 
That would be possible but I was worried the cable wouldn't be protected between the house and shed.

Also is there any way to work out how much power a ring is going to use. I am putting in 3 double sockets and worked it out that at any one time each socket will only be using 13a, however in all possibility each socket could have 2 x 13a appliances in. Then there is the possibility of people putting multimpl adaptors in these sockets............on and on :( What is the best way to estimate?

Thanks for your reply
 
Can you not protect the cable in the house by a 100ma RCBO...don't know if they exist but my 2 cents worth
Or thinking about it a seperate RCD enclosure if you cant get an RCBO
 
hey mate, im in the process of doing a similar thing. put the armoured cable on a 40a mcb on the unprotected side of cu, armour doesnt need to be rcd protected. Then fit your garage cu. Y not fit a 32 a breaker and do a ring main. Then u will easily be able to cope with all those items plugged in.Robo
 
The cable will be burried at the regulation depth and I have just been given a roll of 'Warning Buried Cable' tape from a friend who works for a major instalation company.

I will have a look at sourcing an rcbo as the original consumer unit is a bit dated. If not, I will fit a 40a MCB to the non-rcd side.

Finally I have decided to go for 3 core to run a seperate earth to the shed as well as using the armouring.

Thanks for all your help, it's a relief to know I am not too far off the mark. Never realised how nerve-racking my first "real" job would be.
 
That would be possible but I was worried the cable wouldn't be protected between the house and shed.

Also is there any way to work out how much power a ring is going to use. I am putting in 3 double sockets and worked it out that at any one time each socket will only be using 13a, however in all possibility each socket could have 2 x 13a appliances in. Then there is the possibility of people putting multimpl adaptors in these sockets............on and on :( What is the best way to estimate?

Thanks for your reply

If you have a 32A ring in the shed and it trips from overcurrent then the whole system back to the house would have to be up rated . If it was a real concern couldn't you go for 50 amp mcb and 2 or 3 ring circuits lol.
 

Reply to Help putting power to a shed!! in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
770
I fitted a Mem MR30 Pod and MCB, about ÂŁ75 for both.
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top