E
eskimo39
Hi this will be my first job for myself since qualifying and just would like a little assurance if possible.
A friend has a garden shed 40 meters from his house and would like sockets and lighting putting in. I am thinking 6mm2 SWA 3 core going from his original house CU (protected by rcd and 40a mcb) to a Wylex 2way Garage Consumer with RCD in the shed. Inside the shed 3 x metal clad double sockets on a 2.5mm ring with 20a MCB and a couple of lights on 1.5mm protected by 6a mcb.
I have done a few calculations and estimate load to be approx 8kw (3 sockets at 13a with voltage at 230v giving 8280w) Also on the length of cable I estimate voltdrop to be 9 volts.
Would this be o.k???
In the garage there will be a fridge on one socket, a freezer on another and one spare for lawnmover/hedgetrimmer etc.
Any suggestions/alterations would be greatly appreciated.
A friend has a garden shed 40 meters from his house and would like sockets and lighting putting in. I am thinking 6mm2 SWA 3 core going from his original house CU (protected by rcd and 40a mcb) to a Wylex 2way Garage Consumer with RCD in the shed. Inside the shed 3 x metal clad double sockets on a 2.5mm ring with 20a MCB and a couple of lights on 1.5mm protected by 6a mcb.
I have done a few calculations and estimate load to be approx 8kw (3 sockets at 13a with voltage at 230v giving 8280w) Also on the length of cable I estimate voltdrop to be 9 volts.
Would this be o.k???
In the garage there will be a fridge on one socket, a freezer on another and one spare for lawnmover/hedgetrimmer etc.
Any suggestions/alterations would be greatly appreciated.