Bradzz
inspected a job, service head 3p 4 wire.
100A BS88.
meter tails 25mm2 ccc 101A
out meter into 2 * henly blocks.
out the henly blocks split into 2 supplies, 16mm2 singles, ccc method B 76A.
1 supply goes to 2* db fed into bottom db then linked to top db via main switch as photo.
2 supply goes into a addaptable box into 2 connector blocks 30A linked to 10mm2 MI cable not sure what that is feeding unable to locate but from what they say it goes of into a tower block? N/V ccc of MI 82A thermo coverd.
what codes would you place on this set up ?.
cheers for any help that can be given my mind has gone blank, and i need to input some wording in to the obs section but trying to keeps it to the min not long winded.
MI cable has no means of Isolation. except the main cutout fuse.
16mm2 on a 100A head.
should this not be 25mm2 from meter to ccu and MI cable.
or better still 3 p meter to ryfield 63A then to loads, or 3 isolators. just asking?.
100A BS88.
meter tails 25mm2 ccc 101A
out meter into 2 * henly blocks.
out the henly blocks split into 2 supplies, 16mm2 singles, ccc method B 76A.
1 supply goes to 2* db fed into bottom db then linked to top db via main switch as photo.
2 supply goes into a addaptable box into 2 connector blocks 30A linked to 10mm2 MI cable not sure what that is feeding unable to locate but from what they say it goes of into a tower block? N/V ccc of MI 82A thermo coverd.
what codes would you place on this set up ?.
cheers for any help that can be given my mind has gone blank, and i need to input some wording in to the obs section but trying to keeps it to the min not long winded.
MI cable has no means of Isolation. except the main cutout fuse.
16mm2 on a 100A head.
should this not be 25mm2 from meter to ccu and MI cable.
or better still 3 p meter to ryfield 63A then to loads, or 3 isolators. just asking?.