Hi, please can you see if this is correct for what I am trying to do.
I want 1 ring main circuit for sockets and another for lighting.
This is for a test lab that I am setting up at home.
The CU didn't come with any instruction so I want to make sure that I am doing it right and using the correct cabling.
Here is a picture :
[ElectriciansForums.net] Help wiring Garage Consumer Unit
Here is a picture :
Why would you want a lighting ring? a radial circuit would be the best option for a lighting circuit, and I suggest 1.5mm2 for the lights, not 2.5mm2, just saying.
Got a suspicion the OP is the same chap that said the college he attended used a PSU.
Sorry it was just the way I worded it.
I want 1 main ring for the sockets and another being a radial for the lighting.
Some people say 1mm is adequate for lighting but I don't mind using 1.5mm if I have to.
The feed to the CU is coming from a 13a plug as per the discussion we have the other week about setting up my lab.
Why put a ring anyway - designed decades ago, old hat. I would consider radial sockets in 2.5 but you must replace the 32A MCB with 20A; design depends on the required socket load. As Pete999 states 1.5 for the lights, also in radial.
I want 1 main ring for and another being a radial for the lighting.
The feed to the CU is coming from a 13a plug.
Use a flex, rather than twin and earth cable for the supply cable, 13 amp plug tops are not designed to accept twin and earth cable.
So, what you have planned is totally pointless.
The circuit protection is on the 13A plug, so the 32A MCB in the garage will never ever in a million years trip because the maximum current will only ever be no more than 13amp.
So there is no point having a ring final, again because the current is limited to 13A.
Also I expect that the socket that the plug is in (at the house end?) is already RCD-protected? So there's no point in the RCD in the garage either.
So you could have saved your money on that garage unit, just run in the cable to a string of sockets and used a ÂŁ3 FCU to provide the light switch and feed.
I think the OP intends to build a testing board, to practice his ability for carrying out tests, it's not an ideal scenario, but I guess he will have account for the discrepancies, at least I think that's what he intends to do, but then again in this mad world of DIY electrics, who knows?
Reply to Help wiring Garage Consumer Unit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
462 excerpt below. The incoming supply is via a electrical plant room to the block of flat, each flat has a standard DNO cutout fuse but no...