Hey everyone i have a couple of questions about bonding and the running of a 1.5mm cable.

I know you earth the towel rad, bath and hold and cold pipes in a bathroom, but am i right in saying i dont need to sup bond the pipes or anything in the kitchen?

Also can i run a 1.5mm lighting cable for a 1 metre cable run in a 3 by 3 inch box section with the gas pipe in that supplys the boiler.

Thanks.
 
Sup bonding not required if protected by r.c.d. If carrying out any work to the circuit in question then chances are you will have to protect it by an r.c.d. Nothing wrong with running the cables up the boxing if they are properly supported... NOT cable tied to the gas pipe!!!
 
There must be a separation of 25mm between gas pipes and cables.(OSG 2.3).
You are mixed up on supplementary bonding.
Supplementary bonding is only required in special locations as defined in Bs 7671 which does not include kitchens.
Supplementary bonding may be omitted in bath/shower rooms provided-
1. All circuits in the bath/shower room are RCD protected
2. Required disconnection times are met for all circuits within the bath/shower room.
3. A continuity reading is obtained of <1667 ohms between conductive parts and extraneous conductive parts within the bath/shower room.
Regs 701.415.2

Extraneous conductive parts are metallic services entering the special location, generally metal baths and sinks are not extraneous conductive parts unless they are in contact with structural metallic parts of the building,unlikely in a domestic situation
 

Reply to help with 1.5mm cable in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
167
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Good question now to start with thermosetting insulated conductors are not tri-rated that is something different. Table 4E1A deals with this type...
Replies
1
Views
290
T
  • Article
New plumbing & heating system advice Hello, I'm installing a new central heating & plumbing system and just wanted to run through my design...
Replies
0
Views
293
Tommyh311
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top