Not had the chance to read every reply on this but it sounds like the reason it was running slower was because in star, it only had 230v on its windings which were designed for 400v. In effect it was almost stalling. Then when the delta kicked in, it had the full 400v and ran at its designed speed.
4kW motor is well able to be run of a DOL starter. If you didn't want to get another starter you could connect it in delta and connect the 3 cables to the load side of the RUN contactor (see the diagram on a previous page). Just make sure that the overload setting is within range about 8amp.
I wouldn't bother with an invertor unless the customer wants to vary the speed.