Had a go at a past paper and come across a few questions that i could do with a hand on!! your help would be much appreciated!!! Thanks

1.A SELV circuit is to be tested for electrical separation from a low voltage circuit which
shares the same pvc conduit containment system. State the
a) test voltage to be applied (1 mark)
b) conductors between which the test is carried out. (2 marks)

2.A 230 V circuit containing a surge protection device is to be tested for insulation resistance and the device cannot be disconnected. State the
a) conductors between which the test is carried out 1mark
b)test voltage applied 1mark
c)minimum acceptable resistance. 1mark

3.State the minimum IP rating for each of the following.
a)The top surface of an accessible distribution board 1mark.
b) The front face of a domestic consumer
15 Explain
a) the effect on earth fault protection provided by a BS EN 60898 circuit breaker if it is connected in the neutral conductor only 1mark
b) why the effect in a) above occurs. 2marks
unit. 1mark
c) An internal barrier within a distribution board. 1mark


 
Had a go at a past paper and come across a few questions that i could do with a hand on!! your help would be much appreciated!!! Thanks

1.A SELV circuit is to be tested for electrical separation from a low voltage circuit which
shares the same pvc conduit containment system. State the
a) test voltage to be applied (1 mark)
b) conductors between which the test is carried out. (2 marks)


500v DC
all live conductors and all live conductors to earth

you can find the rest out your self ;-)
 
Upvote 0
Check the BRB on testing only a couple of pages and testing when surge protective devices can not be disconnected is covered you need to read that.

IP codes you will get these questions and you need to know IPXXD IP4X IP2X IPXXB GN3page 42 get to know these along with the other popular ones.

Re the neutral conductor in the protective device.

You need to know your earth fault path as this question comes up time after time and you can get 15 easy marks drawing it and identifying the main parts.

Basically if the neutral is in the protective conductor the mcb will not trip as when a earth fault occurs it does not go down the neutral conductor AS THE NEUTRAL IS NOT PART OF THE EARTH FAULT PATH.


1 Point of fault
2 CPC of cct
3 MET
4 Earthing caonductor TT Mass of earth TN Metalic return.
5 Main earth electrode of transformer Star point
6 Windings of transformer.
7 Line conductor back to point of fault but via MCB which would of now tripped .

Hope this helps
 
Upvote 0
Had a go at a past paper and come across a few questions that i could do with a hand on!! your help would be much appreciated!!! Thanks

1.A SELV circuit is to be tested for electrical separation from a low voltage circuit which
shares the same pvc conduit containment system. State the
a) test voltage to be applied (1 mark)
b) conductors between which the test is carried out. (2 marks)


500v DC
all live conductors and all live conductors to earth

you can find the rest out your self ;-)



SELV - Separated Extra Low Voltage, pretty sure its 250v dc for ELV
 
Upvote 0

Reply to help with a few 2391 questions!!! in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
430
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
He is after the four options for 1 and 2 of the multiple choice exam, probably optimistic someone will know this. Your question 3 in incomplete to...
Replies
2
Views
1K
  • Question
I believe that it is incorporated into the 5 days. But will double check. Thanks.
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top