Hi Guys,
I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used.
The fuse board is an MEM Memera 2000
the downstairs ring is on a 32A 60898 MCB, protected by a 61008 RCD 100A 30mA
there are 2 other circuits on the same RCD which are the upstairs rings on a 32A 60898, and the shower also on a 32A 60898
The customer had this problem before I came and had already tried replacing the washing machine and getting the same problem.
Yet we cant find any fault so I'm absolutely stumped, is there anything I've forgotten to do?
Thank you in advance, I'm loosing hair over this problem haha
Test results for Downstairs socket ring
R1 0.57
RN 0.57
R2 0.95
R1+R2 0.38
Zs 0.63
RCD 1/2x didn't trip
RCD 1x 27.8ms
- we have carried out fault finding and also EICR'd the whole house with perfect results,
- we have tried plugging in the washing machine upstairs which is the same RCD and it didn't trip. and also on another circuit in the garage on a different RCD which also didn't trip (both times the washing machine stayed in the same position in the kitchen under the worktop and was just plugged into different sockets via an extension lead
- we have also tightened all connections on the downstairs ring assuming that maybe the washing machine vibrating could have caused a loose connection and tried fault finding again and cant find any problems
- we have also tested for overload by unplugging every other thing on the circuit and it still trips
- we have also replaced both the RCD and the MCB and still it keeps tripping
- I have tried plugging into other sockets on the same circuit and it still trips
- I have also tried replacing the socket its plugged into just in case
R1 0.57
RN 0.57
R2 0.95
R1+R2 0.38
Zs 0.63
RCD 1x 27.8ms