LearnerDave
Hiya guys.
I am learning about earthing, bonding and cpc’s at the moment, and I am getting a bit stuck with using the armour of SWA as a CPC. Iwonder if anybody would mind helping me by reading this, and correct what I have got wrong so I can make sure I understand it properly.
If I had a 2 core 16mm2 SWA cable. I read that this has a armour CSA of 46mm2. From reading threads in this forum I understand that steel has a stronger resistance compared to copper by a factor of approx. 9. Am I right in dividing 46 by 9 this would give a comparison to copper of 5.1mm2?
My confusion comes when I look at 543.1.4 and table 54.7
If I look at the table for 16mm2 line conductor, I would need a 16mm2 copper CPC. Allowing for the difference in resistance as above I would: 16 x 9 = 144mm2 for a steel CSA equivalent.
If I look at the table 54.7 for protective conductor not the same material as the line conductor and follow the calculation (k1/k2) X S
I make k1 to be 115 Using table 43.1 for copper line conductor in thermoplastic at 70’
I make k2 to be 51 Using table 54.4 for steel in 70’C thermoplastic
(115/51) x 16 = 36mm2
My confusion is that calculating the x9 method means that using the armour of the SWA would be massively undersized, yet using table 54.7 the armour would be acceptable.
I know I am making some stupid mistake but just can’t see the wood for all the trees at the moment. Any help would be really appreciated.
Dave
Dave