Hi guys. I am currently working in a large warehouse doing some investigating after originally doing an energy survey. When I first got here I isolated every submain but still got 30a on each phase. I originally thought someone was illegally tapping off but now think it could be something else.

I have taken apart a main busbar chamber and can see it feeding 4 boards. However I have also traced another set of wires to a large switch controlling a bank of capacitors. On testing this is drawing 30a per phase.

Why would there be a large bank of capacitors now a days. The warehouse has all new lighting with capacities built in for correction and other than that it is mainly only ring mains. Did older lighting require these banks of capacitors or were/are they used for something else?

Also when I turn them off, I am only saving 70a so would this mean they are been used somewhere although not correctly.

Thanks in advance for any help
 
Hi guys. I am currently working in a large warehouse doing some investigating after originally doing an energy survey. When I first got here I isolated every submain but still got 30a on each phase. I originally thought someone was illegally tapping off but now think it could be something else.

I have taken apart a main busbar chamber and can see it feeding 4 boards. However I have also traced another set of wires to a large switch controlling a bank of capacitors. On testing this is drawing 30a per phase.

Why would there be a large bank of capacitors now a days. The warehouse has all new lighting with capacities built in for correction and other than that it is mainly only ring mains. Did older lighting require these banks of capacitors or were/are they used for something else?

Also when I turn them off, I am only saving 70a so would this mean they are been used somewhere although not correctly.

Thanks in advance for any help

Seems to me as if they were/are being used for phase correction - probably for lighting. Flourescents used to be connected in this way on large installs, and other plant requiring power factor correction too.

Capacitors are funny animals - in that you may well get current readings from the dissipation of current once you've isolated them - are you sure you're not reading discharge current, in this case, rather than supply current? The way to tell is to identify which way the current is flowing - e.g. are you getting a negative figure, or a positive one, and which way round is your ammeter connected (or are you getting current readings via a clamp meter)?

The other (obvious) thing to suggest, is that clearly you've got phase connected to the capacitors in some way - where do the capacitors feed on to? Can you trace the wiring at all?

Just some basic thoughts.
 
If you decide to take them out be careful as capacitors can hold a monster charge and will blow your hand off. you can short them to blow the energy or if you leave them long enough they will lose it on their own.
 
If they're only connected to the lighting system, then maybe once upon a time they may have had something to do with the emergency lighting system???


Or maybe there was a lot of industrial machinery present at one time.....
 
I learnt about power factor correction at college but unfortunalty remember bery little of it. There have never been any motors there only really lighting & sockets. Could it be perhaps they were there to somehome help balance the 3 phase supply when it was designed. Now the original design is long gone, could they be causing an opposite effect?
 
Woweee.

PFC is a complex subject to discuss. There's many reasons it could be used.

As you say, it may no longer be needed.

Essentially, power factor correction works by balancing the real power flowing in a circuit with the apparent power (harmonics and such).

I think the best I can do is link you here to WIkipedia for a better explanation that I can manage.

Seems, either way you're dealing with passive power factor correction, and probably for lighting after all.

Simple way of checking if it is still needed at all is to take it out of circuit (safely) and see what effect it has on the installation.
 
I learnt about power factor correction at college but unfortunalty remember bery little of it. There have never been any motors there only really lighting & sockets. Could it be perhaps they were there to somehome help balance the 3 phase supply when it was designed. Now the original design is long gone, could they be causing an opposite effect?

Yes. Inductive loads (from motors and fluorescent lighting) can cause voltage to lead the current. Capacitors have the opposite effect so they are put in to get the voltage and current back in phase and have a power factor closer to 1 (unity). If some or all of the inductive load is now missing the current could now be leading the voltage. Leading to too much current being drawn in the circuits concerned.
 
Yes. Inductive loads (from motors and fluorescent lighting) can cause voltage to lead the current. Capacitors have the opposite effect so they are put in to get the voltage and current back in phase and have a power factor closer to 1 (unity). If some or all of the inductive load is now missing the current could now be leading the voltage. Leading to too much current being drawn in the circuits concerned.

That would be my conclusion as well
Lagging power factor at some distant time with condensers to compensate,but situation is now different and the current being read is charge and discharge of those condensors
They are probably now un required and would be economical to dis connect
 
Thanks for all the help guys. I am going there tomorrow to start changing lights etc for energy efficient ones. I am quite convinced that they are no longer required as I shut them off at around 3pm and there were no ill effects noticable. Only real difference was that the total load drawn went from 180A across all theree phases to just under 110A. Nothing of any real load ever been used in there.

The only bad side is that this seems to have been going on for the last 6 years, wasting around 70A 24/7 (although this could be more as the total load in the morning with all boards isolated was 90A) I have done a little calculation and it would seem at 17P per KWh it is costing over ÂŁ2k per month. Again I have been told that their average electricity bill has been ÂŁ9K per quarter.

I am going to look at taking them out in the future but will just isolate them totally tomorrow and leave it a while to see if they notice any changes bad or good.

Thanks again for all your help.
 
Thanks for all the help guys. I am going there tomorrow to start changing lights etc for energy efficient ones. I am quite convinced that they are no longer required as I shut them off at around 3pm and there were no ill effects noticable. Only real difference was that the total load drawn went from 180A across all theree phases to just under 110A. Nothing of any real load ever been used in there.

The only bad side is that this seems to have been going on for the last 6 years, wasting around 70A 24/7 (although this could be more as the total load in the morning with all boards isolated was 90A) I have done a little calculation and it would seem at 17P per KWh it is costing over ÂŁ2k per month. Again I have been told that their average electricity bill has been ÂŁ9K per quarter.

I am going to look at taking them out in the future but will just isolate them totally tomorrow and leave it a while to see if they notice any changes bad or good.

Thanks again for all your help.

You will only notice the drop in power consumption. The Power factor correction equipment was probably installed at the INSISTANCE of the power provider. without it the meters would not have measured the true power consumption, as to to this properly the voltage and current must not be phase shifted with respect to one another. In the past it was often the case that a factory owner would intentionally disconnect the PFC kit to save money. Some even reorted to removing the PFC capacitors from ALL of the flourescent fittings as well. Must have saved a fortune,
 
My understanding of power factor is that if it is bad ie particularly leading or lagging then you have a larger apparent power meaning that a larger current than necessary is flowing. This has implications for cable sizes and protective devices but not for the energy consumed. It also is a big problem for generating companies as they have to supply larger currents than are actually used which is very wasteful for them and this why they can insist on PF correction measures. I didn't think that there would be particularly more energy used other than the extra heat lost in the cables due to the larger current flowing. ie the customer is being charged for the true power (kW) and not the apparent power(kVA) . Or have i already forgotten what i learnt at college?
 

Reply to Help with capacitors in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

  • Question
I would agree that the motor is by far the best part to replace. if it is powered and not turning then it is broken. Keep it simple!
Replies
1
Views
1K
P
  • Article
Large floor tile adhesive help Hi all, My 1st post and just wanting some help/reassurance on a DIY bathroom refurb. I’m putting down...
Replies
0
Views
229
parrydave
P

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top