Guys, I have an assignment which I am struggling with but which should be easy and have read loads of books I keep going around in circles. Can you please put me back on the tracks.
The task is for the design of a RFC in a garage with the routing clipped a few centimetres below the ceiling and taken down single 20mm conduit from this height to each of the 4 double outlets. The conduit is to provide additional mechanical protection.
The Ref method is method B because of the conduit limiting the capacity for the 2,5mm cable to 23A (From 30A) [Table7.1(ii) or Table F5(i) OSG], as this is a ring to be protected by a 30 breaker this is still ok. However, as both cables go down the same conduit to the outlet there should be a grouping factor to consider. Looking at Appendix F (OSG) there is a general equation It=In/(CaxCgxCixCf), but I have three issues.
Firstly there appears to be no Cg factor for a conduit delivery in Table F3 OSG. Where can I find this info.
Secondly the numbers in table F3 get smaller the more cables, and as they go on the bottom line of the equation they will increase the It value where I would have expected it to decrease.
Thirdly once I get the grouping factor how do I apply it to the Ref Method B data to get a revised capacity.
Thanks
The task is for the design of a RFC in a garage with the routing clipped a few centimetres below the ceiling and taken down single 20mm conduit from this height to each of the 4 double outlets. The conduit is to provide additional mechanical protection.
The Ref method is method B because of the conduit limiting the capacity for the 2,5mm cable to 23A (From 30A) [Table7.1(ii) or Table F5(i) OSG], as this is a ring to be protected by a 30 breaker this is still ok. However, as both cables go down the same conduit to the outlet there should be a grouping factor to consider. Looking at Appendix F (OSG) there is a general equation It=In/(CaxCgxCixCf), but I have three issues.
Firstly there appears to be no Cg factor for a conduit delivery in Table F3 OSG. Where can I find this info.
Secondly the numbers in table F3 get smaller the more cables, and as they go on the bottom line of the equation they will increase the It value where I would have expected it to decrease.
Thirdly once I get the grouping factor how do I apply it to the Ref Method B data to get a revised capacity.
Thanks