Just been doing some college work.
Was calculating if supp equip bonding was required in a bathroom. The formula given for an mcb is R < 50V / Ia.
Ia being the fault current for a particular mcb to disconnect in a certain time.
My question is, as there are likely to be various circuits in a bathroom, which mcb rating would you use as the calculation. Would it be the shower circuit mcb as this is likely to be the highest rated and thus require more fault current to disconnect within a certain time.
I know to the 17th, that supp bonding is not required if rcd protected and all that. This is a theory question and was just wondering what you guys thought.
Cheers
Craig
Was calculating if supp equip bonding was required in a bathroom. The formula given for an mcb is R < 50V / Ia.
Ia being the fault current for a particular mcb to disconnect in a certain time.
My question is, as there are likely to be various circuits in a bathroom, which mcb rating would you use as the calculation. Would it be the shower circuit mcb as this is likely to be the highest rated and thus require more fault current to disconnect within a certain time.
I know to the 17th, that supp bonding is not required if rcd protected and all that. This is a theory question and was just wondering what you guys thought.
Cheers
Craig