Just been doing some college work.

Was calculating if supp equip bonding was required in a bathroom. The formula given for an mcb is R < 50V / Ia.

Ia being the fault current for a particular mcb to disconnect in a certain time.

My question is, as there are likely to be various circuits in a bathroom, which mcb rating would you use as the calculation. Would it be the shower circuit mcb as this is likely to be the highest rated and thus require more fault current to disconnect within a certain time.

I know to the 17th, that supp bonding is not required if rcd protected and all that. This is a theory question and was just wondering what you guys thought.

Cheers
Craig
 
Supp bonding is used when there is an increased risk of electric (ie bathrooms) and the resistence between parts should be less than 0.05 ohms.

another use is when disconnection times cannot be met, so if the circuit you are concerned with will not disco in the required time then supp bonds are installed using the formula you provided and the fault current taken for that device.

Althouh now under 17th most requirements are met to avoid installing sup bonds at all (although personally I will always do it regardless.

Thats my view/ understanding im pretty sure youll get other opinions.
 
Upvote 0
That pretty much covers it. Working to 17th now you`d have an 30mA RCD protecting all ccts in the location so you could supplant the Ia for I^n to give you R< 50v x 0.03

Understand your Q was a theoretical one but in the real world the 0.05 ohms is the biggie - resistance between all exposed & extraneous conductive parts, & between those & the MET to be that or less.

So, if calculating for Supplementary Bonding required due to increased shock risk, then establishing no simultaneously accessible parts have greater than 50mOhm resistance between them is what is required

Whereas, when Supplementary Bonding so disconnection times are met then this is required for each cct in the location
 
Last edited by a moderator:
Upvote 0
Just been doing some college work.

Was calculating if supp equip bonding was required in a bathroom .

In theory if no RCD then yes, supplementary bonding is required regardless of any calculations (701.415.2). But then 701.411.3.3 says RCD's are required regardless :confused:

The formula given for an mcb is R < 50V / Ia.
Ia being the fault current for a particular mcb to disconnect in a certain time.

This formula is to confirm if supplementary bonding is effective, not to see if its required or not.
R is the resistance between accessible exposed conductive parts and extraneous conductive parts (415.2.2).

Would it be the shower circuit mcb as this is likely to be the highest rated

The higher the value of Ia the lower the value for R, so its fair to assume that provided the shower complies than the others will if their measurement is not a greater value.
 
Last edited by a moderator:
Upvote 0

Reply to help with college formula please! in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top